I am having problems with my American steam ASD-A
everytime I turn it on the circuit breaker pops. I have the electrician here and he can't figure it out. Can you help me?


Title: Re: steam generator keeps popping the circuit breaker
Post by: Earl on April 10, 2012, 09:35:28 AM
You didn't give us much information. I'm guessing the generator has worked well for the past few years and this just came on suddenly. There are not too many reasons the circuit breaker would pop. I would guess wire size or breaker size but if it has been working for some time that should not be an issue. Perhaps a short somewhere or most likely the element burned out which I think might cause that.


Title: Re: steam generator keeps popping the circuit breaker
Post by: Michael on April 10, 2012, 11:38:59 AM
No, this is a new installation. Generator was still in the box and I'm just now getting around to installing it.


Title: Re: steam generator keeps popping the circuit breaker
Post by: Earl on April 10, 2012, 11:41:57 AM
Okay, that's a whole different situation. Ask your electrician what kind of power he is running to the generator? It should be 240V, 50 AMP breaker and at least #8 wire.


Title: Re: steam generator keeps popping the circuit breaker
Post by: Michael on April 10, 2012, 12:25:00 PM
I spoke to the contrator and he said he is running 240V on a 60 amp GFCI and #8 wire.


Title: Re: steam generator keeps popping the circuit breaker
Post by: Earl on April 10, 2012, 12:34:38 PM
Okay, I'm starting to get the picture. Tell your electrician to remove the GFCI and hook up generator directly and let me know how that works out for you.


Title: Re: steam generator keeps popping the circuit breaker
Post by: Michael on April 10, 2012, 01:48:16 PM
Hey Earl, It's working like a charm now. I thought everything required a GFCI.
Now if I can just figure out how to work this control.


Title: Re: steam generator keeps popping the circuit breaker
Post by: Earl on April 10, 2012, 01:52:09 PM
Unless a manufacturer tells you differently never put a GFCI on a steam generator. It will cause you problems every time.
Regarding the control; I will send you a manual.


Title: Re: steam generator keeps popping the circuit breaker
Post by: mnolan9941 on June 01, 2012, 03:30:21 PM
i have a ss-140 thermasol steam generator,,since 2001 on a 2pole 50amp gfci breaker. it just started popping the breaker recently. i changed the breaker out and it still pops the breaker as soon as the steam begins to flow. any ideas on a fix?


Title: Re: steam generator keeps popping the circuit breaker
Post by: Earl on June 01, 2012, 04:41:12 PM
Take another look at the answers from April 10Th. If you replaced the GFCI breaker with another GFCI breaker you will still have the same issue. There indeed may be another cause but first try hooking you generator to a non GFGCI breaker and see what happens.


Title: Re: steam generator keeps popping the circuit breaker
Post by: Jennifer on June 04, 2012, 08:35:46 AM
All steam bath generator manufacturers state to not use a GFCI breaker.  It will trip nearly everytime.  The installation requires a non-GFCI breaker.